Industrial plant consists of 4-motors and transformer. Two induction motors and two synchronous motors are installed with the following data: The slip range of induction motors is between: s =...

1 answer below »
Industrial plant consists of 4-motors and transformer. Two induction motors and two synchronous motors are installed with the following data: The slip range of induction motors is between: s = XXXXXXXXXXThe induction motor at rated load power factor is between PF = XXXXXXXXXXlagging. The induction motor rated sizes are available of 100, 150, 200, & 250 hp. The efficiency of the induction motors is between 80%-90% The synchronous motor rated sizes are available of 100, 150, 200, &250 kW. The synchronous motor at rated load power factor is between PF = 0.80 lagging-0.80 leading. The efficiency of the synchronous motors is between 85%-92% The motor poles are available of 2 or 4. The voltage source is VLL = 480V, 60Hz. The total load torque of the plant is 2900 N.m. The total power factor, PF, at the secondary side of the transformer is 1 = PF = 0.95 lagging.
Document Preview:

King Fahd University of Petroleum & Minerals Electrical Engineering Department DESIGN PROJECT Semester XXXXXXXXXXThis project is posted on WebCT on 28/04/2013 and it is due on 14th May 2013 Industrial plant consists of 4-motors and transformer. Two induction motors and two synchronous motors are installed with the following data: The slip range of induction motors is between: s = XXXXXXXXXXThe induction motor at rated load power factor is between PF = XXXXXXXXXXlagging. The induction motor rated sizes are available of 100, 150, 200, & 250 hp. The efficiency of the induction motors is between 80%-90% The synchronous motor rated sizes are available of 100, 150, 200, &250 kW. The synchronous motor at rated load power factor is between PF = 0.80 lagging-0.80 leading. The efficiency of the synchronous motors is between 85%-92% The motor poles are available of 2 or 4. The voltage source is VLL = 480V, 60Hz. The total load torque of the plant is 2900 N.m. The total power factor, PF, at the secondary side of the transformer is 1 = PF = 0.95 lagging. 1. Design the motor specification such as size, pole numbers, slip, efficiency, and PF based on the data available above. (note: Motors from each type cannot be the same rating) 2. Select proper transformer which can handle the total load taking to consideration 70% of load factor plus losses. 3. Show all your calculations in detail (power in all forms, currents, speeds, voltages, etc) 4. Typing report should be submitted. M1M2M3M4480V, 60HzTransformerInductionMotorInductionMotorSynchronousMotorSynchronousMotor

Answered Same Day Dec 22, 2021

Solution

Robert answered on Dec 22 2021
116 Votes
DESIGN AND IMPLEMENTATION OF UNIVERSAL CONTROLLER FOR POWER CONTROL APPLICATIONS
We are going to design a motor using the following specifications of induction motors and synchronous motors which is already given are as follows
Induction motors:
Slip range of induction motors is between: s = 0.03-0.05
Induction motor at rated load power factor is between PF = 0.75-0.85 lagging
Induction motor rated sizes are available of 100, 150, 200, & 250 hp
Efficiency of the induction motors is between 80%-90%
Synchronous motors:
Synchronous motor rated sizes are available of 100, 150, 200, &250 kW.
Synchronous motor at rated load power factor is between PF = 0.80 lagging-0.80 leading.
Efficiency of the synchronous motors is between 85%-92%.
Motor poles are available of 2 or 4.
Voltage source is VLL = 480V, 60Hz.
Total load torque...