Figure 1 shows the network diagram of a 132kV power system. The network has three buses and two generating units. The loads of (l.O+jO.35) pu and (3.2+J1.2) pu are connected at bus 2 and 3...

1 answer below »

Figure 1 shows the network diagram of a 132kV power system. The network has three buses and two generating units. The loads of (l.O+jO.35) pu and (3.2+J1.2) pu are connected at bus 2 and 3 respectively. The generator connected at bus 2 injects 1.2 pu of active power.
V,=i.042
S = 3.2+ j1.2
Figure 1:132kV system - all values are given in pu with Vb=132kV and Sb=100MVA
(a) Perform two, Newton-Raphson method based, load flow iterations (without using computer
simulations). Calculate voltage at each bus and power losses of the system in actual units. Clearly
show the load flow calculation steps.
(b) Perform two, Fast Decoupled method based, load flow iterations (without using computer
simulations). Calculate voltage at each bus and power losses of the system in actual units. Clearly
show the load flow calculation steps.
Document Preview:

Created with an evaluation copy of Aspose.Words. To discover the full versions of our APIs please visit: https://products.aspose.com/words/ Figure 1 shows the network diagram of a 132kV power system. The network has three buses and two generating units. The loads of (l.O+jO.35) pu and (3.2+J1.2) pu are connected at bus 2 and 3 respectively. The generator connected at bus 2 injects 1.2 pu of active power. V,=i.042 S = 3.2+ j1.2 Figure 1:132kV system - all values are given in pu with Vb=132kV and Sb=100MVA Perform two, Newton-Raphson method based, load flow iterations (without using computer simulations). Calculate voltage at each bus and power losses of the system in actual units. Clearly show the load flow calculation steps. Perform two, Fast Decoupled method based, load flow iterations (without using computer simulations). Calculate voltage at each bus and power losses of the system in actual units. Clearly show the load flow calculation steps.

Answered Same Day Dec 20, 2021

Solution

Robert answered on Dec 20 2021
123 Votes
Solution:
Representing the impedances of the bus system
BUS CODE

IMPEDANCE
1-2 0+j0.18
2-3 0+j0.32
1-3 0+j0.24
Schedule of generation and load as given is:
BUS CODE

ASSUMED VOLTAGE GENERATION LOAD
MW MVAR MW MVAR
1-2 1.042+j0 0 0 0 0
2-3 1+j0 1.2 0 1 j0.35
1-3` 1+j0 0 0 3.2 j1.2
Calculating bus admittance matrix:
BUS CODE IMPEDANCE

ADMITTANCE

1-2 j0.18 -5.556j
2-3 j0.32 -3.125j
1-3 j0.24 -4.1667j
Forming bus admittance matrix
ADMITTANCE CODE

ADMITTANCE FORMULA ADMITTANCE VALUE
-9.722j
5.556j
4.1667j
5.556j
-8.681j
3.125j
4.1667j
3.125j
-7.2917j
Hence matrix can be written as:
[



]
[



]
Now development of load flow equations:
For any bus:


∑
Now
Hence separating real and imaginary parts:
∑{ ( ) ( )}
∑{ ( ) ( )}
Now from nodal admittance matrix we get:
B E f


( ) ( ) ( ) ( )
( ) ( )
Now we have f1=0, f2=0, f3=0
( ) ( ) ( )
( ) ( ) ( )

( ) ( )


( ) ( ) ( ) ( )
( ) ( )
Now we have f1=0, f2=0, f3=0
( ) ( ) ( )
( ) ( ) ( )

( ) ( )


( ) ( ) ( ) ( )
( ) ( )
Now we have f1=0, f2=0, f3=0
( ) ( ) ( )
( ) ( ) ( )

( )
( ) ( ) ( ) ( )
( ) ( )
Now we have f1=0, f2=0, f3=0
( ) ( ) ( )
( ) ( ) ( )

For iteration 2:


*
( )

∑
∑


{
( )



}


{
( ( ))

}



|
|



{
( )



}


{
( ( ))

}



|
|


Hence we get:

|
|| | | | ( ) |
|

| | ( ) |
||
| | | ( )

( ) ( )
( ( ))

( ) ( ) ( )



( )

|
|| | | | ( ) |
|

| | ( ) |
||
| | | ( )

( ) ( )
( ...
SOLUTION.PDF