4. A load, 100 m from a 415 V Supply Authority point is connected by a35 mm2 pvc/swa/pvc copper cable. The current rating is 119 A and thevolt drop per ampere metre is 1.1 mV. If the load current is...

1 answer below »
4. A load, 100 m from a 415 V Supply Authority point is connected by a35 mm2 pvc/swa/pvc copper cable. The current rating is 119 A and thevolt drop per ampere metre is 1.1 mV. If the load current is 90 A,determine whether the volt drop at the load is within the 17th Edition ofthe IEE Wiring Regulations 5% limit. Using TABLE 1, calculate theearth loop impedance, minimum fault current (neglect the supply/earthimpedance) and select an appropriate fuse for the circuit with reference toB.S. 88 part 2 (see FIGURE 3, Lesson 4 - 4).
Answered Same Day Dec 24, 2021

Solution

David answered on Dec 24 2021
122 Votes
for 35mm2 pvc/swa copper cable volt drop per ampere meter is 1.1mV
first we need to find voltage drop in cable so we should not take actual cu
ent rating to calculate
actual cu
ent rating=119A load cu
ent=90A
length of cable=100m
voltage drop in cable=1.1*90*100*10-3
...