Great Deal! Get Instant $10 FREE in Account on First Order + 10% Cashback on Every Order Order Now

1. A salient pole machine supplies a load of 1.2 p.u. at unity power factor to an infinite bus whose voltage is maintained at 1.05 p.u. The machine excitation voltage is computed to be 1.4 p.u. when...

1 answer below »

1. A salient pole machine supplies a load of 1.2 p.u. at unity power factor to an infinite bus whose voltage is maintained at 1.05 p.u. The machine excitation voltage is computed to be 1.4 p.u. when the power angle is 25°. Evaluate the direct-axis and quadrature-axis synchronous reactances.

2. Solve Problem 3.18 using MATLABTM.

Problem 3.18

A salient pole machine supplies a load of 1.2 p.u. at unity power factor to an infinite bus whose voltage is maintained at 1.05 p.u. The machine excitation voltage is computed to be 1.4 p.u. when the power angle is 25°. Evaluate the direct-axis and quadrature-axis synchronous reactances.

Answered Same Day Dec 25, 2021

Solution

Robert answered on Dec 25 2021
137 Votes
Solution
The active and reactive power equations for the salient-pole machine
are given by Eq. (3.61) and (3.62). Using the given data we obtain
2= (1 .4) (1.05) . 250 + (1 .
05) 2 (� _ � ) . 500 1 . X sm 2 X X sm d q d
0= (1 .4�1 .05) cos250 _ (1 .05)2 ( CO�25° + Si�25 ) d d q
These...