Solution
David answered on
Dec 25 2021
Running Header: A Study on District Cooling System in Hong Kong 1
A Study on District Cooling System in Hong Kong
A Study on District Cooling System in Hong Kong 2
Table of Contents
ABSTRACT 4
1. CHAPTER 1 – INTRODUCTION 5
1.1. Introduction / Background 5
1.2. Aims and Objectives 10
1.3. Research Methodology 11
2. CHAPTER 2: LITERATURE REVIEW 13
2.1. Introduction 13
2.2. Review 14
2.2.1. Benefits of District Cooling 15
2.2.2. Key issue of Design and Design process 19
2.2.3. Peak-Day Hourly Load Profile 20
2.2.4. Chiller And Pumping Configuration 21
3. CHAPTER 3: RESEARCH METHODOLOGY 25
3.1. Brief Introduction 25
3.2. Methodology Used 26
4. CHAPTER 4: RESEARCH / INVESTIGATION 27
4.1. Introduction 27
4.2. Implementation of Methodology Used 27
4.3. Description of Data Collected 27
4.4. Analysis & Findings 30
5. CHAPTER 5: CONCLUSIONS AND RECOMMENDATION 43
5.1. Introduction 43
A Study on District Cooling System in Hong Kong 3
5.2. Conclusions and Recommendations 43
5.3. Recommendations For Further Research 44
References 45
A Study on District Cooling System in Hong Kong 4
ABSTRACT
In the context of Hong Kong, the overall consumption of electricity is increasing on an annual
asis each year and in specific the utilization of consumption of electricity with respect to
Heating Ventilation Air Conditioning (“HVAC”) systems contribute to 30 per cent of the overall
electricity consumption levels as has been described in report titled “Hong Kong Energy End use
data 2015”. This signifies that the HVAC system need to be accorded more focus over the
performances in terms of efficiency levels as well as sustainable development. In this context,
the overall objectives concerning this dissertation titled “A Study on District Cooling System in
Hong Kong” comprised the following, (i) A detailed undertaking and comprehensive comparison
etween the conventional form of chilled water based cooling system with respect to water
cooled as well as air cooled based system, and (ii) In addition to this comparative assessment, it
is also planned to undertake investigation of the design related consideration as well as the
various difficulties relating to the implementation of DCS form of cooling system. The specific
methodology applied to undertake the study include collection of relevant data and pursue
suitable analysis shall pertaining to a case study based research study wherein the DSC based
cooling system found in Hong Kong was identified, studied in detail and relevant collected to
address the twin objectives of this study. The overall findings, analysis and outcome of the study
are presented in detail.
A Study on District Cooling System in Hong Kong 5
1. CHAPTER 1 – INTRODUCTION
1.1. Introduction / Background
In the context of Hong Kong, the overall consumption of electricity is increasing on an
annual basis each year and in specific the utilization of consumption of electricity with
espect to Heating Ventilation Air Conditioning (“HVAC”) systems contribute to 30 per cent
of the overall electricity consumption levels as has been described in report titled “Hong
Kong Energy End use data 2015” (Shu et al, 2010; Yang et al, 2014; Chua et al, 2013). This
signifies that the HVAC system need to be accorded more focus over the performances in
terms of efficiency levels as well as sustainable development (Shu et al, 2010; Yang et al,
2014; Chua et al, 2013).
.
For any city across tropics, the requirement of air conditioning services becomes an essential
form of services across all forms of buildings (Shu et al, 2010; Yang et al, 2014; Chua et al,
2013). In addition, the increase in population that is always growing and also the continuous
development in economic aspects in a combined manner increase the overall demand levels
elating to HVAC systems (Shu et al, 2010; Yang et al, 2014; Chua et al, 2013). In present
times, the prevailing vision amongst the HVAC engineers across Hong Kong are not just in
offering comfortable form of indoor environment, but in addition to enhance and optimize
the overall efficiency levels relating to HVAC systems (Shu et al, 2010; Yang et al, 2014;
Chua et al, 2013). On account of the circumstances aforesaid, any newer form of technology,
alternative for sustainable operations, improvement over efficiency levels as an approach
towards which any HVAC system could be applied need to suitably become the primary area
A Study on District Cooling System in Hong Kong 6
of focus as well as one that is well worth in being investigated like that of the District
Cooling System (“DCS”) which shall be studied in a detailed manner and the relative
advantages shall be demonstrated over the course of this dissertation (Shu et al, 2010; Yang
et al, 2014; Chua et al, 2013).
DCS essentially refers to a centralized form of large scale HVAC system which shall
generate thermal energy by way of the circulation of chilled water from one central source
towards multiple set of facilities or buildings by way of a piping network for this distribution
using suitable thermal insulation (Shu et al, 2010; Yang et al, 2014; Chua et al, 2013). More
importantly, DCS represents the system that is energy efficient as the same integrates various
chiller plants across each of the buildings / facilities to single centralized production centre
for cooling (Shu et al, 2010; Yang et al, 2014; Chua et al, 2013). When compared with that of
the conventional forms of air-cooled and air-conditioning forms of systems as well as
individual air-conditioning systems based on water cooled models that use the cooling
towers, DCS has proven consumption levels of electricity that is 35 per cent and 20 per cent
lesser respectively. (EMSD, 2002; Shu et al, 2010; Yang et al, 2014; Chua et al, 2013)
The government of Hong Kong implemented the initial DCS across the Kai Tak
Development during the year 2010, for providing the cooling system for private / public
commercial establishments (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). This DCS has
een established for providing cooling systems for varied set of buildings / facilities - retail
uildings, offices, hotels and government buildings with an aggregate floor area totalling to
oughly 1.73 million Sq. meters as well as comprising of close to 39 kilo meters of total pipe
A Study on District Cooling System in Hong Kong 7
network for distribution as well as two separate plant rooms (Gang et al, 2015a; Xia et al,
2011; Ge et al, 2011). The overall capacity of cooling to the maximum extent that shall be
generated by this DCS aggregates to about 83250 RT while all of the buildings under the
scope of this DCS are fully occupied and are in operation during summer. (Environment
Bureau, 2013; Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). The DCS is essentially
categorized as two distinct form of chiller plants as in centralized form of cooling sources
(Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). Subsequently, 26 of the chillers shall be
installed in a gradual and shall be put in operation (Tam, 2014; Gang et al, 2015a; Xia et al,
2011; Ge et al, 2011).
In the context of Hong Kong, air-cooled based water chillers use ambient air to be the heat
sink which rated with the temperature levels of 35 degree Celsius as well as the concerned
co-efficient of performance (“COP”) (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011),
epresenting the ratio of the cooling output to the power input, ranges across the values
etween 2.6 and 2.9 comprising the condenser fan powers (Gang et al, 2015a; Xia et al,
2011; Ge et al, 2011). Although, the water cooled form of chiller plant using sea water form
of cooling have the rated water proceeding with temperature of about 28 degree Celsius and
moving out with the temperature levels of 33
degree Celsius and in this case COP levels
concerning with chiller plants could be between 4.1 and 5.2, or sometimes much higher
(EMSD, 2012; Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011)
The implementation and setup of DCS are being undertaken in an increasing trend across
globe and the same has prompted the government of Hong Kong in also implementing the
A Study on District Cooling System in Hong Kong 8
same system across the Kai Tak Development (“KTD”) as well as attempt in applying over
other newer developments across the Hong Kong (Gang et al, 2015a; Xia et al, 2011; Ge et
al, 2011). DCS could aid in serving varied forms of the building like that of hospitals,
esidential buildings, commercial buildings / facilities, etc. (Gang et al, 2015a; Xia et al,
2011; Ge et al, 2011). A DCS could be developed in a rapid manner across the globe on
account of varied set of reasons (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). In
addition to the minimization of the space occupied by chiller plant across a building,
efficiency levels of energy could also be substantially enhanced and hence the cost of
operation, as well as cost of maintenance could be significantly reduced (Gang et al, 2015a;
Xia et al, 2011; Ge et al, 2011). In having evaluated the consultancy study produced and
published by the entity called Ove Arup & Partners Hong Kong Limited, the same indicated
that DCS being applied across SEKD could result in the saving of energy at about 19 per cent
and 35 per cent respectively when compared to that of standalone systems of air conditioning
operating over cooling towers as well as air cooled form of chillers (EMSD, 2003; Gang et
al, 2015a; Xia et al, 2011; Ge et al, 2011).
In the context of this dissertation, relevant case study shall be pursued and undertaken with
an aimed for evaluating comparative assessments between energy saving from DCS as
against the conventional form of cooling systems (Gang et al, 2015a; Xia et al, 2011; Ge et
al, 2011). In essence DCS was originally designed and constructed for serving several
uildings / facilities as a group which includes the larger scale centre for sport, high rise
structure of a hotel, as well as the office building across Wan Chai wherein continuous form
of cooling are essential all through the months in a year (Gang et al, 2015a; Xia et al, 2011;
A Study on District Cooling System in Hong Kong 9
Ge et al, 2011). In buildings that are existing, there are no requirements in terms of the
calculation of cooling load as well as in addition the loading profile in actual could be
determined on the basis of the data arising from the cooling systems that are prevailing
(Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). On account of this fact that these
uilding essential are of varied forms, their respective peak demands shall not be across same
or similar time and hence the factor of diversity need to be considered in focus towards the
estimation of cooling load as well as this specific factor need to account in addition to the
variations concerning the occupancy (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). The
centre for sports having three different storeys is spread across 190,00 Square Meter of gross
level floor area as well as floor to floor level of area being 6 meter and in a typical sense
offering wider range in terms of the leisure facilities indoor like that of squash courts,
asketball courts, and various other such facilities (Gang et al, 2015a; Xia et al, 2011; Ge et
al, 2011). A chiller plant has been installed across the ground floor offering chilled water
towards the respective fan coil units, primary air units and air handling units by way of 9,000
kilo Watt peak level cooling load (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). It had
een observed that this centre for ports has been occupied with people over the full working
hours between 07:00 Hours and 22:00 Hours (Gang et al, 2015a; Xia et al, 2011; Ge et al,
2011). Although, there have been very limited people occupancy at this centre for sports
etween 07:00 Hours and 18:00 Hours while there had been peak level occupancy between
18:00 hours and 22:00 hours. In the other aspect, the other buildings being planned to be
catered to, that is hotel as well as commercial building, by way of DCS possess 2500 kilo
Watt as well as 3000 kilo Watt cooling loads in respective manner (Gang et al, 2015a; Xia et
al, 2011; Ge et al, 2011). This commercial building / facility being planned to be catered to is
A Study on District Cooling System in Hong Kong 10
solely utilized for the purposes of accommodating offices which are essentially occupied
during the normal working business hours between 07:00 hours and 18:00 hours as well as
the levels of occupancy at this commercial building is almost close to zero post the business
hours of 18:00 hours (Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). By way of
simulating this building with the newer new DCS on the basis of the prevailing scenario, the
same is aimed for quantitatively accessing whether these district form of cooling system
could attained the levels of performances that are more efficient and economical as compared
to the conventional forms of cooling systems (Gang et al, 2015a; Xia et al, 2011; Ge et al,
2011).
A DCS aids in serving these varied buildings in a simultaneous manner and on account of the
same in consequence DCS shall have the peak level cooling loads that are lower as compared
to sum of the each peak level cooling loads of the various buildings (Gang et al, 2015a; Xia
et al, 2011; Ge et al, 2011). Thus, the overall diversity element ingrained needs to be
evaluated while determining the capacity of cooling relating to district systems of cooling
(Gang et al, 2015a; Xia et al, 2011; Ge et al, 2011). The factors of diversity relates to that of
atio concerning the aggregate sum of maximum level loads for each of the individual
uildings towards the peak level demands concerning with the DCS (Gang et al, 2015a; Xia
et al, 2011; Ge et al, 2011).
1.2. Aims and Objectives
The overall objectives concerning this dissertation titled “A Study on District Cooling
System in Hong Kong” is in undertaking detailed and comprehensive comparison between
https:
en.wikipedia.org/wiki/Ratio
A Study on District Cooling System in Hong Kong 11
the conventional form of chilled water based cooling system with respect to water cooled as
well as air cooled based system. It is essential for finding out and determining if the DCS
form of cooling system is comparatively friendly to environment and more profitable and
thus suitable alternative for the conventional forms of chilled water based cooling system to
deal with that of cooling demand for the future of Hong Kong. In addition to this
comparative assessment, it is also planned to undertake investigation of the design related
consideration as well as the various difficulties relating to the implementation of DCS form
of cooling system. As the HVAC systems account for over 50 per cent power consumption
overall (Duanmu et al, 2013; Haiwen et al, 2010a; Abdullah et al, 2013), it shall not just be
the cost related implications for the owner of a building but also from an environmental
sustainability perspective as the required electricity are generated by relying over non-
enewable and greenhouse gas emitting fossil fuels, specifically natural gas / coal as is the
case across Hong Kong. For the purposes of reducing the costs relating to operation by owner
of building as well as towards protection of the environment, the overall objective of the
dissertation is in comparing the DSC form of cooling system with that of the conventional
forms of cooling system as well as study potential relating to energy saving in the DSC when
used across the regions located in sub-tropical area with higher density population similar to
that of Hong Kong.
1.3. Research Methodology
Research methodology refers to the overall design of the research being undertaken, the
methods employed to collect the relevant primary and / or secondary data, and method of
analysis undertaken on the data so collected to address the research objectives by
determining suitable outcomes (He
& Anderson, 2014; Jackson, 2015; Robson &
A Study on District Cooling System in Hong Kong 12
McCartan, 2016). In this context the research method employed for this study derives from
the basis or the overall objective of this study which includes, undertaking detailed and
comprehensive comparison between the conventional forms of chilled water based cooling
system with respect to water cooled as well as air cooled based system (He
& Anderson,
2014; Jackson, 2015; Robson & McCartan, 2016). It is essential for finding out and
determining if the DCS form of cooling system is comparatively friendly to environment and
more profitable and thus suitable alternative for the conventional forms of chilled water
ased cooling system to deal with that of cooling demand for the future of Hong Kong (He
& Anderson, 2014; Jackson, 2015; Robson & McCartan, 2016). In addition to this
comparative assessment, it is also planned to undertake investigation of the design related
consideration as well as the various difficulties relating to the implementation of DCS form
of cooling system (He
& Anderson, 2014; Jackson, 2015; Robson & McCartan, 2016). As
the HVAC systems account for over 50 per cent power consumption overall (Duanmu et al,
2013; Haiwen et al, 2010a; Abdullah et al, 2013), it shall not just be the cost related
implications for the owner of a building but also from an environmental sustainability
perspective as the required electricity are generated by relying over non-renewable and
greenhouse gas emitting fossil fuels, specifically natural gas / coal as is the case across Hong
Kong (He
& Anderson, 2014; Jackson, 2015; Robson & McCartan, 2016). For the purposes
of reducing the costs relating to operation by owner of building as well as towards protection
of the environment, the overall objective of the dissertation is in comparing the DSC form of
cooling system with that of the conventional forms of cooling system as well as study
potential relating to energy saving in the DSC when used across the regions located in sub-
tropical area with higher density population similar to that of Hong Kong (He
& Anderson,
A Study on District Cooling System in Hong Kong 13
2014; Jackson, 2015; Robson & McCartan, 2016). The specific methodology applied to
undertake the study, collect relevant data and pursue suitable analysis shall pertain to a case
study based research study wherein the DSC based cooling system found in Hong Kong shall
e identified, studies in detail and relevant data shall be collected to address the twin
objectives of this study (He
& Anderson, 2014; Jackson, 2015; Robson & McCartan, 2016).
Essentially, the data that shall be collected in this regard shall be secondary data with both
qualitative as well as quantitative forms of data types (He
& Anderson, 2014; Jackson,
2015; Robson & McCartan, 2016). On the basis of the study so undertaken and relevant data
collected, qualitative form of analysis shall be pursued to address the objectives of this
esearch study (He
& Anderson, 2014; Jackson, 2015; Robson & McCartan, 2016).
2. CHAPTER 2: LITERATURE REVIEW
2.1. Introduction
The overall objectives concerning this dissertation titled “A Study on District Cooling
System in Hong Kong” is in undertaking detailed and comprehensive comparison between
the conventional form of chilled water based cooling system with respect to water cooled as
well as air cooled based system. It is essential for finding out and determining if the DCS
form of cooling system is comparatively friendly to environment and more profitable and
thus suitable alternative for the conventional forms of chilled water based cooling system to
deal with that of cooling demand for the future of Hong Kong. In addition to this
comparative assessment, it is also planned to undertake investigation of the design related
consideration as well as the various difficulties relating to the implementation of DCS form
of cooling system. As the HVAC systems account for over 50 per cent power consumption
A Study on District Cooling System in Hong Kong 14
overall (Duanmu et al, 2013; Haiwen et al, 2010a; Abdullah et al, 2013), it shall not just be
the cost related implications for the owner of a building but also from an environmental
sustainability perspective as the required electricity are generated by relying over non-
enewable and greenhouse gas emitting fossil fuels, specifically natural gas / coal as is the
case across Hong Kong. For the purposes of reducing the costs relating to operation by owner
of building as well as towards protection of the environment, the overall objective of the
dissertation is in comparing the DSC form of cooling system with that of the conventional
forms of cooling system as well as study potential relating to energy saving in the DSC when
used across the regions located in sub-tropical area with higher density population similar to
that of Hong Kong.
2.2. Review
DSC form of cooling system are either being planned to be established or else already being
used across varied set of organizations like that of private sector development organization,
public sector development organization, power utilities, etc. (Duanmu et al, 2013; Haiwen et
al, 2010a; Abdullah et al, 2013) and other companies in recent time, leading to overall
eduction across the cost of energy consumption (Duanmu et al, 2013; Haiwen et al, 2010a;
Abdullah et al, 2013). Although, most parts of the country continues to use and rely over the
conventional forms of cooing systems (Duanmu et al, 2013; Haiwen et al, 2010a; Abdullah et
al, 2013).
In case of Hong Kong, significant levels of attention are actually being paid over the
application concerning the DSC form of cooling systems towards the purposes of cooling
A Study on District Cooling System in Hong Kong 15
across newer as well as large scale of developments (Duanmu et al, 2013; Haiwen et al,
2010a; Abdullah et al, 2013). Hence, for the purposes of addressing the critical issue
pertaining to issues of technical nature, instrumentation relating to metering, controls,
distribution systems, operation of the DSC plant, risk related considerations, overall design
process and designing with respect to the piping as well as insulation materials and also the
methods of connection, reviewing of the earlier studies that are hence being pursued
(Duanmu et al, 2013; Haiwen et al, 2010a; Abdullah et al, 2013).
2.2.1. Benefits of District Cooling
The objectives relating to this specific sub-section of the literature review is in
understanding comprehensively the overall benefits as well as risks pertaining to the
implementation of the DSC form of...