XXXXXXXXXXpdf Question 1 (10) Your consulting firm is requested to undertake a fire safety engineering assessment of a multi- storey commercial building with a large atrium. The atrium connects multi-floors. A schematic layout of the building is given in Figure 1. One of the design solutions is to use a natural ventilation system for smoke control in the atrium. a) In your opinion, what will be the appropriate modelling tool for predicting smoke movement in the building and evaluating the performance of the smoke control system? Justify your decision (no more than 100 words). (5 Marks) b) Discuss the advantages and disadvantages of using your proposed modelling tool in comparison to other possible alternatives (<200 words). (5 Marks) Figure 1. Building layout. Question 2 (40) The engineering team has decided to conduct a preliminary analysis using the CFAST zone model for the atrium in Question 1. Assume that the Christmas decoration at the centre of the atrium is on fire. The fire is of fast growth and the maximum heat release rate is 8 MW. Tasks: a) Use the relevant standard to determine the smoke vent and makeup air vent sizes. (5 Marks) b) Develop and explain your modelling strategy. (5 Marks) (<100 words) c) Produce a SmokeView diagram of your simulation compartments. Tabulate them with enclosure labels and dimensions, vent opening labels, dimensions and connections. (5 Marks) d) Execute the model. Produce the EXCEL graphics of the input heat release rate, output of smoke layer height, temperature, CO concentration and smoke extinction coefficient in the smoke layer as functions of time in the atrium. (15 Marks) e) Discuss the results (<200 words) (10 Marks) Question 3 (10) A beam smoke detector was placed near the ceiling of the atrium [see Figure 1(b)]. The activation transmittance of the detector is 0.65. What time will the detector activate? Discuss the result. Question 4 (40) a) Conduct a literature search for two publications (year 2010 onwards) on any one or a combination of the following topics (25 Marks) i) New development in fire modelling and validation; ii) Fire modelling application in forensic investigation; iii) Building element fire resistance modelling; iv) Bushfire modelling. Present, in your own word, a summary of the articles searched. Discuss the key features of the articles (background, aim, methodology, findings, conclusions and recommendations). State if there is any connection between the two articles. Range of total number of words: XXXXXXXXXXTables and diagrams may be used. b) Conduct a literature review on different building materials (concrete, steel, timber, cladding materials, insulation materials, plasterboards) and summaries the key properties (such as Specific Heat (kJ/kg.K), Conductivity (W/m.K), Density (Kg/m3), Heat of combustion (kJ/kg), Emissivity) that can be used in FDS modelling, and discuss the effect of these properties on fire performance (15 Marks). NOTE: The articles you searched should not be in the reference lists of the lecture notes. The following tools and sources may be used: Western Sydney University library online search: http://library.westernsydney.edu.au/main/ Google Scholar: http://scholar.google.com.au/ IAFSS Fire Research Engine: http://www.iafss.org/fire-research-engine/ NIST BFRL publication online: http://fire.nist.gov/bfrlpubs/ The journals may include, but not limited to Fire Safety Journal Fire Technology Journal of Fire Sciences International Journal of Wildland Fires The above journals are accessible via WSU library
Answered 3 days After Jun 02, 2022

Solution

Dr Shweta answered on Jun 05 2022
84 Votes
Ans 1 A) Smoke management system is an integral part of Fire Safety Engineering (FSE) because the major casualties during building fires occu
ed due to smoke. The appropriate modelling tool used here for smoke control, prediction of smoke movement and evaluation of smoke control system in the building is the large-eddy simulation CFD code based Fire Dynamics Simulator (FDS) model. This model is chosen because it is a field fire model with smoke analysis specifically structured for rectangular mesh as shown in figure 1. It is cost effective and versatile model for huge spacious buildings like shopping-centre, mega- complexes with easy computer simulation.
Ans 1 B) Atria are example of large spaces where conventional zone approaches like ASMET are not sufficiently effective. The suitable modelling tool for atrium is the field based-Fire Dynamics Simulator (FDS) modelling tool. Its advantages and disadvantages in comparison to other modelling tools are as follows:
1. Advantages-
· The FDS modelling tool is versatile and cost effective.
· It provides numerical simulation of fire-generated smoke movement in large complex space where conventional zone-model is not effective. And can covers huge spacious buildings like mega-complexes, convention centres, etc. efficiently.
· It provides the transient development of the smoke profile, temperature distribution profile and velocity field.
· It provides high level of safety and can link outside building weather conditions and smoke and fire development.
· It provides effective strategy or controlling the smoke filling, gravity venting and smoke exhaust.
· Its tenability system approach provides complete protection to occupants with no exposure to smoke during evacuation in case of building fire.
2. Disadvantages-
The main disadvantage of this tool is that it is applicable only for the low-speed flow. It is not suitable for flow speeds approaching the speed of sound as in case of explosions, choke flow at nozzles, and detonations.
Ans 2a) The floor area mentioned in figure 1 is 30 m * 20 m = 600m2. The effective vent size should be 3.5% of maximum floor area so equal to 21m2 and the make-up air vent size should be 1.2 % of maximum floor area so equal to 7.2m2.
2b) here we applied the zone fire model –the ASMET model to calculate the amount of smoke evolved the distribution pattern of smoke, dispersion of fire gases and temperature attained throughout the complex. This model consists of a set of equations and provides the analysis of smoke management systems for big spaces like atria.
2c) Smoke view diagram-Vent opening
2d) EXCEL graphics of the factors - input heat release rate, output of smoke layer height, temperature, CO concentration and smoke extinction coefficient in the smoke layer as functions of time in the atrium is as follows:
2 e) With the evolution of fire, the temperature, heat release and co concentration increases in the atrium.
Ans 3 A beam smoke detector is a device that utilizes a projected beam of light to detect smoke across large areas. It typically acts as a fire indicator of buildings. The beam smoke detector consists of a transreciever unit that projects, monitors and transreciever a beam reflected across the protected area. The detector works on the principle of light obscuration. Given that the activation transmittance of the detector is 0.65 it means 65% of incident light which is transmitted .which shows the presence of smoke in the system and hence after detecting the 35% light obscuration the detector will activate within 15-30...